Which protection is employed for generator rating from 1 MVA to 5 MVA?
Answer & step-by-step solution
C — Balanced earth fault. This is the protection scheme associated with the 1–5 MVA generator range in the supplied paper.
Correct answer: C — Balanced earth fault
How balanced earth-fault protection operates
Balanced earth-fault protection detects earth faults inside a defined generator protection zone. In a typical arrangement, the residual current obtained from the three phase current transformers is compared with the current measured by a neutral current transformer. CT ratios, polarities and connections are selected so that the relay currents balance for healthy operation and faults outside the protected zone.
For normal balanced operation, the phasor sum of the three line currents is approximately zero. During an external earth fault, the corresponding phase-residual and neutral-current signals should balance at the relay. Little operating current therefore flows through its measuring element.
An earth fault within the CT-defined zone disturbs this balance. A difference or spill current flows through the relay, which initiates tripping when its operating threshold is exceeded. The protected zone and sensitivity depend on the actual CT arrangement and generator neutral-earthing system.
The examination associates this relatively economical scheme with generators rated 1 MVA to 5 MVA . The rating range is a textbook selection guide, not a universal design rule. Real generator protection is selected using winding arrangements, earthing, fault-current levels, required coverage and coordination.
Quick Trick
Internal stator earth fault → look for a differential/balanced earth-fault scheme.
Why Other Options Are Wrong
A is aimed at phase unbalance/negative-sequence conditions. B and D are time-graded overcurrent/earth-fault approaches and are less specifically matched to the keyed small-generator internal earth-fault scheme. C is the source-keyed scheme.
Common Mistake
Assuming ‘balanced earth fault’ means the fault itself is balanced; the word refers to the protection scheme’s current balance.

1 MVA से 5 MVA रेटिंग वाले जनरेटर के लिए कौन-सी सुरक्षा प्रयुक्त होती है?
उत्तर और चरणबद्ध हल
C — संतुलित अर्थ फॉल्ट सुरक्षा। प्रश्नपत्र में 1–5 MVA श्रेणी के जनरेटरों के लिए यही योजना बताई गई है; बड़े जनरेटरों में प्रायः डिफरेंशियल सुरक्षा होती है।
विस्तृत हल (मूल भाषा में)
Correct answer: C — Balanced earth fault
How balanced earth-fault protection operates
Balanced earth-fault protection detects earth faults inside a defined generator protection zone. In a typical arrangement, the residual current obtained from the three phase current transformers is compared with the current measured by a neutral current transformer. CT ratios, polarities and connections are selected so that the relay currents balance for healthy operation and faults outside the protected zone.
For normal balanced operation, the phasor sum of the three line currents is approximately zero. During an external earth fault, the corresponding phase-residual and neutral-current signals should balance at the relay. Little operating current therefore flows through its measuring element.
An earth fault within the CT-defined zone disturbs this balance. A difference or spill current flows through the relay, which initiates tripping when its operating threshold is exceeded. The protected zone and sensitivity depend on the actual CT arrangement and generator neutral-earthing system.
The examination associates this relatively economical scheme with generators rated 1 MVA to 5 MVA . The rating range is a textbook selection guide, not a universal design rule. Real generator protection is selected using winding arrangements, earthing, fault-current levels, required coverage and coordination.
Quick Trick
Internal stator earth fault → look for a differential/balanced earth-fault scheme.
Why Other Options Are Wrong
A is aimed at phase unbalance/negative-sequence conditions. B and D are time-graded overcurrent/earth-fault approaches and are less specifically matched to the keyed small-generator internal earth-fault scheme. C is the source-keyed scheme.
Common Mistake
Assuming ‘balanced earth fault’ means the fault itself is balanced; the word refers to the protection scheme’s current balance.

1 MVA થી 5 MVA રેટિંગવાળા જનરેટર માટે કયું રક્ષણ વપરાય છે?
જવાબ અને પગલાવાર ઉકેલ
C — સંતુલિત અર્થ ફોલ્ટ રક્ષણ. પ્રશ્નપત્રમાં 1–5 MVA શ્રેણીના જનરેટર માટે આ જ યોજના દર્શાવી છે; મોટા જનરેટરમાં સામાન્ય રીતે ડિફરન્શિયલ રક્ષણ હોય છે.
વિગતવાર ઉકેલ (મૂળ ભાષામાં)
Correct answer: C — Balanced earth fault
How balanced earth-fault protection operates
Balanced earth-fault protection detects earth faults inside a defined generator protection zone. In a typical arrangement, the residual current obtained from the three phase current transformers is compared with the current measured by a neutral current transformer. CT ratios, polarities and connections are selected so that the relay currents balance for healthy operation and faults outside the protected zone.
For normal balanced operation, the phasor sum of the three line currents is approximately zero. During an external earth fault, the corresponding phase-residual and neutral-current signals should balance at the relay. Little operating current therefore flows through its measuring element.
An earth fault within the CT-defined zone disturbs this balance. A difference or spill current flows through the relay, which initiates tripping when its operating threshold is exceeded. The protected zone and sensitivity depend on the actual CT arrangement and generator neutral-earthing system.
The examination associates this relatively economical scheme with generators rated 1 MVA to 5 MVA . The rating range is a textbook selection guide, not a universal design rule. Real generator protection is selected using winding arrangements, earthing, fault-current levels, required coverage and coordination.
Quick Trick
Internal stator earth fault → look for a differential/balanced earth-fault scheme.
Why Other Options Are Wrong
A is aimed at phase unbalance/negative-sequence conditions. B and D are time-graded overcurrent/earth-fault approaches and are less specifically matched to the keyed small-generator internal earth-fault scheme. C is the source-keyed scheme.
Common Mistake
Assuming ‘balanced earth fault’ means the fault itself is balanced; the word refers to the protection scheme’s current balance.