Regarding the selection of industrial cables, consider the following:1.XLPE insulated cables have a higher continuous operating temperature than PVC cables.2.The short-circuit rating of a cable is independent of the insulation material.3.Voltage drop calculation is mandatory for selecting long cable runs.Which of the statements given above is/are correct?
⚑ Report issue
Found a wrong answer, translation, image or source problem? Send it to editorial review.
Industrial cable selection must satisfy current-carrying capacity, voltage drop, installation conditions and short-circuit withstand. XLPE insulation generally permits a higher continuous conductor temperature than PVC. Key relation: Voltage drop≈I(R cosφ+X sinφ)L; adiabatic short-circuit relation I²t≈k²S².
Exam focus: Check ampacity, voltage drop and short-circuit withstand together. Common trap: Cable short-circuit rating is not independent of insulation temperature limits.
Formula / Key Relation
Voltage drop≈I(R cosφ+X sinφ)L; adiabatic short-circuit relation I²t≈k²S².
Detailed Explanation
Correct Answer: C - 1 and 3 only Quick Concept Explanation Industrial cable selection must satisfy current-carrying capacity, voltage drop, installation conditions and short-circuit withstand. XLPE insulation generally permits a higher continuous conductor temperature than PVC. Key relation: Voltage drop≈I(R cosφ+X sinφ)L; adiabatic short-circuit relation I²t≈k²S².Exam focus: Check ampacity, voltage drop and short-circuit withstand together. Common trap: Cable short-circuit rating is not independent of insulation temperature limits. Statement-wise Verification Statement 1 - Correct.XLPE insulated cables have a higher continuous operating temperature than PVC cables.XLPE insulation generally permits a higher continuous conductor temperature than PVC. Statement 2 - Incorrect.The short-circuit rating…
Correct Answer: C - 1 and 3 only
Quick Concept Explanation
Industrial cable selection must satisfy current-carrying capacity, voltage drop, installation conditions and short-circuit withstand. XLPE insulation generally permits a higher continuous conductor temperature than PVC. Key relation: Voltage drop≈I(R cosφ+X sinφ)L; adiabatic short-circuit relation I²t≈k²S².
Exam focus: Check ampacity, voltage drop and short-circuit withstand together. Common trap: Cable short-circuit rating is not independent of insulation temperature limits.
Statement-wise Verification
Statement 1 - Correct. XLPE insulated cables have a higher continuous operating temperature than PVC cables. XLPE insulation generally permits a higher continuous conductor temperature than PVC.
Statement 2 - Incorrect. The short-circuit rating of a cable is independent of the insulation material. Permissible conductor temperature during a short circuit depends on insulation and cable construction, affecting short-circuit rating
Statement 3 - Correct. Voltage drop calculation is mandatory for selecting long cable runs. Industrial cable selection must satisfy current-carrying capacity, voltage drop, installation conditions and short-circuit withstand.
Core Concept
Industrial cable selection must satisfy current-carrying capacity, voltage drop, installation conditions and short-circuit withstand. XLPE insulation generally permits a higher continuous conductor temperature than PVC. Short-circuit thermal capability depends on conductor material, cross-section and allowable initial/final temperatures, which are linked to insulation construction.
Formula / Key Relationship
Voltage drop≈I(R cosφ+X sinφ)L; adiabatic short-circuit relation I²t≈k²S².
Why the Other Options Are Wrong
Option A is incorrect because it includes incorrect statement(s) 2 and omits correct statement(s) 3. Option B is incorrect because it includes incorrect statement(s) 2 and omits correct statement(s) 1. Option D is incorrect because it includes incorrect statement(s) 2.
Exam Shortcut / Approach
Check ampacity, voltage drop and short-circuit withstand together.
Common Mistake
Cable short-circuit rating is not independent of insulation temperature limits.
Quick Revision
XLPE Temperature Short-Circuit and Voltage Drop is linked with Cable Selection, Cables and Industrial Electrical Systems. Check ampacity, voltage drop and short-circuit withstand together.
Quick Trick
Check ampacity, voltage drop and short-circuit withstand together.
Why Other Options Are Wrong
Option A is incorrect because it includes incorrect statement(s) 2 and omits correct statement(s) 3. Option B is incorrect because it includes incorrect statement(s) 2 and omits correct statement(s) 1. Option D is incorrect because it includes incorrect statement(s) 2.
Common Mistake
Cable short-circuit rating is not independent of insulation temperature limits.
Exam Tip
Check ampacity, voltage drop and short-circuit withstand together.