Balanced Earth-Fault Protection for Small Generators

Which protection is employed for generator rating from 1 MVA to 5 MVA?
⚑ Report issue

Found a wrong answer, translation, image or source problem? Send it to editorial review.

Answer & Explanation
Correct AnswerC. Balanced earth fault

Quick Explanation

C — Balanced earth fault. This is the protection scheme associated with the 1–5 MVA generator range in the supplied paper.

Formula / Key Relation

KEY RELATION / LOGIC: Under healthy or external-fault conditions, the residual of the phase CT currents balances the neutral CT current; an internal earth fault produces differential relay current.

Detailed Explanation

Correct answer: C — Balanced earth fault

How balanced earth-fault protection operates

Balanced earth-fault protection detects earth faults inside a defined generator protection zone. In a typical arrangement, the residual current obtained from the three phase current transformers is compared with the current measured by a neutral current transformer. CT ratios, polarities and connections are selected so that the relay currents balance for healthy operation and faults outside the protected zone.

For normal balanced operation, the phasor sum of the three line currents is approximately zero. During an external earth fault, the corresponding phase-residual and neutral-current signals should balance at the relay. Little operating current therefore flows through its measuring element.

An earth fault within the CT-defined zone disturbs this balance. A difference or spill current flows through the relay, which initiates tripping when its operating threshold is exceeded. The protected zone and sensitivity depend on the actual CT arrangement and generator neutral-earthing system.

The examination associates this relatively economical scheme with generators rated 1 MVA to 5 MVA. The rating range is a textbook selection guide, not a universal design rule. Real generator protection is selected using winding arrangements, earthing, fault-current levels, required coverage and coordination.

Quick Trick

Internal stator earth fault → look for a differential/balanced earth-fault scheme.

Why Other Options Are Wrong

A is aimed at phase unbalance/negative-sequence conditions. B and D are time-graded overcurrent/earth-fault approaches and are less specifically matched to the keyed small-generator internal earth-fault scheme. C is the source-keyed scheme.

Common Mistake

Assuming ‘balanced earth fault’ means the fault itself is balanced; the word refers to the protection scheme’s current balance.

Exam Tip

Generator protection questions often distinguish selective differential/earth-fault schemes from backup time-graded overcurrent schemes.

Continue learningRelated PYQs & Exam ContextExam path, knowledge path and deeper practice links.
1Previous Exam Appearances
6All Related Questions

Previous Exam Appearances

cdn3_digialm_com_per_g21_pub_1722_touchstone_AssessmentQPHTMLMode1(4).PDF2024 12:30 PM - 02:30 PMQ. 10

More Questions From This Concept

PYQ DiscoveryBrowse all verified PYQs
Open Index
Ready for exam mode?Practice this knowledge in Premium Mock Tests
Open Mock Tests →