Reactive Power–Voltage Drop Relationship

The lagging reactive power delivered by a line is proportional to ______ and is independent of ______.
⚑ Report issue

Found a wrong answer, translation, image or source problem? Send it to editorial review.

Answer & Explanation
Correct AnswerC. Line voltage drop; δ

Quick Explanation

C — Line voltage drop; δ. This is the small-angle, predominantly reactive-line approximation; the exact reactive-power expression still contains cos δ.

Formula / Key Relation

QR = (VSVR cos δ − VR²)/X
For small δ: QR ≈ VRΔV/X

Detailed Explanation

Correct answer: C — Line voltage drop; δ

Power flow through a lossless line

Consider a line represented by series reactance X, neglecting resistance and shunt charging. Let VS and VR be sending- and receiving-end voltage magnitudes, with angle difference δ. Using per-phase RMS quantities, the receiving-end powers are:

PR = (VSVR/X) sin δ
QR = (VSVR cos δ − VR²)/X

Positive QR represents lagging reactive power delivered at the receiving end. These equations show that active power depends strongly on angle, while reactive power depends strongly on voltage magnitude.

Step 1: Apply the small-angle approximation. For small δ measured in radians, cos δ ≈ 1. Hence:

QR ≈ (VSVR − VR²)/X

Step 2: Factor out the receiving voltage. Define the voltage-magnitude drop as ΔV = VS − VR:

QR ≈ (VR/X)(VS − VR)
QR ≈ (VR/X)ΔV

At fixed VR and X, lagging reactive power is approximately proportional to voltage-magnitude drop, and δ does not appear in this approximation. Thus option C is intended. The independence is not exact: at larger angles, the cos δ term matters, and resistance also couples voltage, angle, active power and reactive power.

Quick Trick

Real power follows angle; reactive power follows voltage.

Why Other Options Are Wrong

A reverses the dominant dependencies. B reactance affects the magnitude but reactive power is not independent of power angle in the exact expression simply as stated. D does not represent the standard decoupled relation. C matches the normal small-angle approximation.

Common Mistake

Treating the ‘independent of δ’ statement as exact under all operating conditions; it is an approximation associated with a predominantly reactive line and small δ.

Exam Tip

P–δ and Q–V is one of the most useful power-system approximation pairs.

Continue learningRelated PYQs & Exam ContextExam path, knowledge path and deeper practice links.
1Previous Exam Appearances
6All Related Questions

Previous Exam Appearances

cdn3_digialm_com_per_g21_pub_1722_touchstone_AssessmentQPHTMLMode1(4).PDF2024 12:30 PM - 02:30 PMQ. 26

More Questions From This Concept

PYQ DiscoveryBrowse all verified PYQs
Open Index
Ready for exam mode?Practice this knowledge in Premium Mock Tests
Open Mock Tests →