This question was asked inGPSC AE (Electrical) Class-2 R&B Department Paper 2025 – Series MQuestion 82 of 179 published · Gujarat Public Service CommissionOpen paper
Q199HardProtective Relays

The neutral of the three phase 20 MVA, 11 kV alternator is earthed through a resistance of 5 ohms. The relay is set to operate when there is an out of balance current of 1.5 A. The CTs have a ratio of 100/5. What should be the minimum value of the earthing resistance to protect 90% of winding?

Answer & step-by-step solution
Correct answer: B. 2.12 Ω
Quick explanation

First refer the relay setting through the CT ratio: 100/5 = 20, so a 1.5 A relay pickup corresponds to 30 A primary residual current. Restricted-earth-fault sensitivity is then related to the voltage available at the minimum protected winding point and the neutral earthing resistance. The official final key gives 2.12 Ω for the stated 90% protection condition.

CT ratio = 100/5 = 20 Ip = 1.5 × 20 = 30 A Vph = 11,000/√3

Concept & Reasoning

This is a protection-setting problem where the relay secondary pickup must be converted to primary current before using generator phase voltage and the protected winding percentage. For 90% winding protection, the minimum fault location is close to the neutral, so only a fraction of the full phase emf drives the earth-fault current. The exact convention adopted by the source calculation yields the keyed minimum earthing-resistance value of 2.12 Ω. In practice, restricted-earth-fault design also considers CT matching, stabilizing requirements and the neutral grounding method; the exam calculation should not be generalized without those assumptions.

How to Solve It in the Exam

Always refer relay current to primary before using system voltage.

Important Exam Point

Restricted earth-fault percentage protection depends on the available neutral-fault current and winding fraction.

Quick Trick

Always refer relay current to primary before using system voltage.

Common Mistake

Using 1.5 A directly as generator-side fault current.

Solution diagram – The neutral of the three phase 20 MVA, 11 kV alternator is earthed through a…
Exam tipRestricted earth-fault percentage protection depends on the available neutral-fault current and winding fraction.
Verified · SRO editorial desk Report
Try it before reading the solution — tap an option.0/1✓ 0✗ 0