Regarding "Earthing" requirements as per Indian standards, consider the following:1.The earth neutral conductor shall be earthed at the source and at each point of supply.2.The resistance of the earth connection should be as high as possible for safety.3.Periodic testing of earth pits is a mandatory safety requirement.Which of the statements given above is/are correct?

⚑ Report issue

Found a wrong answer, translation, image or source problem? Send it to editorial review.

Sign in to submit a report
Answer & Explanation
Correct AnswerA. 1 and 3 only

Quick Explanation

Protective earthing provides a low-impedance path for fault current and stabilizes exposed conductive parts/neutral references. Earth resistance should be low enough to meet protection requirements and is checked periodically because soil/moisture/corrosion can change electrode performance. Key relation: Touch voltage and disconnection time depend on earthing and protective-device coordination.

Exam focus: Low earth resistance is desirable—not high resistance. Common trap: Never state that high earth resistance improves safety.

Formula / Key Relation

Touch voltage and disconnection time depend on earthing and protective-device coordination.

Detailed Explanation

Correct Answer: A - 1 and 3 only Quick Concept Explanation Protective earthing provides a low-impedance path for fault current and stabilizes exposed conductive parts/neutral references. Earth resistance should be low enough to meet protection requirements and is checked periodically because soil/moisture/corrosion can change electrode performance. Key relation: Touch voltage and disconnection time depend on earthing and protective-device coordination.Exam focus: Low earth resistance is desirable—not high resistance. Common trap: Never state that high earth resistance improves safety. Statement-wise Verification Statement 1 - Correct.The earth neutral conductor shall be earthed at the source and at each point of supply.Low earth resistance…

SEO + Knowledge GraphRelated PYQs & Exam ContextExam path, knowledge path and deeper practice links.
1Previous Exam Appearances
6All Related Questions
99Content Quality

Previous Exam Appearances

Deputy Executive Engineer (Electrical), Class-2, Sports Authority of Gujarat / Assistant Engineer (Electrical), Class-2,2026Q. 197

More Questions From This Concept

PYQ DiscoveryBrowse all verified PYQs
Open Index
Ready for exam mode?Practice this knowledge in Premium Mock Tests
Open Mock Tests →