Rectifier Current and Inverter Extinction-Angle Control

Choose the correct option about dc-link control in HVDC system Statement-1: Current control by controlling delay angle at inverter-end while keeping minimum extinction angle at rectifier-end results in the better voltage regulation. Statement-2: Currents during line faults are automatically limited with rectifier station in current control.
⚑ Report issue

Found a wrong answer, translation, image or source problem? Send it to editorial review.

Answer & Explanation
Correct AnswerC. Statement-1 is False, but Statement-2 is True

Quick Explanation

Normal LCC-HVDC control coordinates the terminals so the rectifier commonly controls DC current through firing angle while the inverter maintains a minimum extinction angle γ. This provides current regulation while preserving commutation margin at the inverter. The correct statement combination is option C.

Formula / Key Relation

Rectifier: constant-current control; inverter: constant-extinction-angle control (normal mode)
Rectifier Current and Inverter Extinction-Angle Control explanatory diagram

Detailed Explanation

Correct Answer

C — Statement-1 is False, but Statement-2 is True

Concept and Reasoning

Normal LCC-HVDC control coordinates the terminals so the rectifier commonly controls DC current through firing angle while the inverter maintains a minimum extinction angle γ. This provides current regulation while preserving commutation margin at the inverter. The correct statement combination is option C.

Calculation / Key Relation

Rectifier: constant-current control

inverter: constant-extinction-angle control (normal mode)

Exam Takeaway

LCC rule of thumb: rectifier controls current, inverter protects γ.

Common Mistake

Do not interchange firing-delay and extinction-angle roles between normal rectifier and inverter control.

Quick Trick

LCC rule of thumb: rectifier controls current, inverter protects γ.

Common Mistake

Do not interchange firing-delay and extinction-angle roles between normal rectifier and inverter control.

Exam Tip

LCC rule of thumb: rectifier controls current, inverter protects γ.

Continue learningRelated PYQs & Exam ContextExam path, knowledge path and deeper practice links.
1Previous Exam Appearances
6All Related Questions

Previous Exam Appearances

QP-112-202425.pdf2024Q. 86

More Questions From This Concept

PYQ DiscoveryBrowse all verified PYQs
Open Index
Ready for exam mode?Practice this knowledge in Premium Mock Tests
Open Mock Tests →