Zero-Sequence Reference and Phase Voltage

Consider following statements: Assertion: When a line-to-line (L-L) fault takes place at the terminals of an open-circuited generator, the phase voltages are sometimes indeterminate though line voltages are always determinable. Reason: During L-L fault, a zero-sequence voltage is always indeterminate. Of these statements:
⚑ Report issue

Found a wrong answer, translation, image or source problem? Send it to editorial review.

Answer & Explanation
Correct AnswerA. Both Assertion and Reason are true and Reason is the correct explanation of Assertion.

Quick Explanation

For an L-L fault there is no zero-sequence current, so the zero-sequence network is not fixed by current flow. At open-circuited generator terminals this can leave the common zero-sequence voltage reference indeterminate even though line-to-line voltages remain uniquely determined. Hence both assertion and reason are true and the reason explains the assertion: option A.

Formula / Key Relation

L-L fault: I0=0; line voltages are independent of common zero-sequence voltage shift
Zero-Sequence Reference and Phase Voltage explanatory diagram

Detailed Explanation

Correct Answer

A — Both Assertion and Reason are true and Reason is the correct explanation of Assertion.

Concept and Reasoning

For an L-L fault there is no zero-sequence current, so the zero-sequence network is not fixed by current flow. At open-circuited generator terminals this can leave the common zero-sequence voltage reference indeterminate even though line-to-line voltages remain uniquely determined. Hence both assertion and reason are true and the reason explains the assertion: option A.

Calculation / Key Relation

L-L fault: I0=0

line voltages are independent of common zero-sequence voltage shift

Exam Takeaway

A common phase-voltage shift cancels in line-to-line voltages.

Common Mistake

Do not infer that indeterminate phase reference makes line voltage indeterminate.

Quick Trick

A common phase-voltage shift cancels in line-to-line voltages.

Common Mistake

Do not infer that indeterminate phase reference makes line voltage indeterminate.

Exam Tip

A common phase-voltage shift cancels in line-to-line voltages.

Continue learningRelated PYQs & Exam ContextExam path, knowledge path and deeper practice links.
1Previous Exam Appearances
6All Related Questions

Previous Exam Appearances

QP-112-202425.pdf2024Q. 179

More Questions From This Concept

PYQ DiscoveryBrowse all verified PYQs
Open Index
Ready for exam mode?Practice this knowledge in Premium Mock Tests
Open Mock Tests →