Calculate the power dissipated in the 8 Ω resistor in the circuit shown in Fig. Q4.
Answer & step-by-step solution
All four branches share the same two nodes, so one node-voltage equation solves the circuit. Let the top-node voltage be V. Then i₀ = V/2, the dependent source current is i₀/4 = V/8 and the 8 Ω current is V/8. KCL gives V = 8 V, hence P₈Ω = V²/8 = 8 W.
Concept Foundation — Why Nodal Analysis Is Ideal Here
Every element in Fig. Q4 is connected between the same top node and the same bottom reference node. That means every branch has the same voltage. Instead of writing several loop equations, define one node voltage V and express each branch current in terms of V.
The circuit also contains a dependent current source . A dependent source is not assigned an arbitrary current; its value must always be written from its controlling variable. Here the controlling current is i₀ through the 2 Ω resistor.
Step 1 — Define the Node Voltage and Controlling Current
Take the bottom conductor as reference (0 V) and the top conductor as V volts. The current i₀ is shown downward through the 2 Ω resistor, so by Ohm’s law:
i_0 = V/2
Step 2 — Express the Dependent Source
The dependent current source arrow is downward and its value is i₀/4. Therefore:
i_d = i_0/4 = (V/2)/4 = V/8
Step 3 — Express the 8 Ω Branch Current
i_8Ω = V/8
Step 4 — Apply KCL at the Top Node
The 6 A source injects current upward into the top node. The three right-hand branch currents leave the top node downward. Hence incoming current = outgoing current:
6 = V/2 + V/8 + V/8
6 = 4V/8 + V/8 + V/8
6 = 6V/8 = 3V/4
V = 8 V
Step 5 — Calculate Power in the 8 Ω Resistor
P = V²/R
P_8Ω = 8²/8 = 8 W
KCL Cross-Check
i_0 = 8/2 = 4 A
i_d = i_0/4 = 1 A
i_8Ω = 8/8 = 1 A
4 + 1 + 1 = 6 A ✓
The branch currents exactly equal the 6 A source current, confirming the node equation and the final answer.
Concept Extension
Dependent sources remain active during normal circuit analysis. Their controlling relationship is part of the circuit physics. The fastest safe workflow is: choose node voltage → write controlling variable → write dependent source → apply KCL → calculate the requested power.
Exam Strategy
When many branches share the same two nodes, first test whether a single-node KCL equation can solve the problem. It is often much faster than mesh analysis.
Quick Trick
Same two nodes → one V. i₀ = V/2, dependent = V/8, 8 Ω current = V/8. KCL → V = 8 V → P = 8 W.
Why Other Options Are Wrong
- B — 16 W: would require |V| = √(16×8) ≈ 11.31 V, which does not satisfy KCL.
- C — 32 W: would require |V| = 16 V, inconsistent with the 6 A source and branch currents.
- D — 64 W: would require |V| ≈ 22.63 V, also impossible from the KCL relation.
Common Mistake
Ignoring the arrow direction, forgetting i₀ = V/2, or using i₀/4 as a constant current independent of V.

चित्र Q4 में दिखाए गए परिपथ में 8 Ω प्रतिरोधक में व्यय शक्ति की गणना कीजिए।
उत्तर और चरणबद्ध हल
A — 8 W। चारों शाखाएँ एक ही दो नोड साझा करती हैं, इसलिए एक नोड-वोल्टेज समीकरण पर्याप्त है। ऊपरी नोड वोल्टेज V हो तो i₀ = V/2, आश्रित स्रोत धारा = V/8 और 8 Ω धारा = V/8। KCL से V = 8 V, अतः P = V²/8 = 8 W।
विस्तृत हल (मूल भाषा में)
Concept Foundation — Why Nodal Analysis Is Ideal Here
Every element in Fig. Q4 is connected between the same top node and the same bottom reference node. That means every branch has the same voltage. Instead of writing several loop equations, define one node voltage V and express each branch current in terms of V.
The circuit also contains a dependent current source . A dependent source is not assigned an arbitrary current; its value must always be written from its controlling variable. Here the controlling current is i₀ through the 2 Ω resistor.
Step 1 — Define the Node Voltage and Controlling Current
Take the bottom conductor as reference (0 V) and the top conductor as V volts. The current i₀ is shown downward through the 2 Ω resistor, so by Ohm’s law:
i_0 = V/2
Step 2 — Express the Dependent Source
The dependent current source arrow is downward and its value is i₀/4. Therefore:
i_d = i_0/4 = (V/2)/4 = V/8
Step 3 — Express the 8 Ω Branch Current
i_8Ω = V/8
Step 4 — Apply KCL at the Top Node
The 6 A source injects current upward into the top node. The three right-hand branch currents leave the top node downward. Hence incoming current = outgoing current:
6 = V/2 + V/8 + V/8
6 = 4V/8 + V/8 + V/8
6 = 6V/8 = 3V/4
V = 8 V
Step 5 — Calculate Power in the 8 Ω Resistor
P = V²/R
P_8Ω = 8²/8 = 8 W
KCL Cross-Check
i_0 = 8/2 = 4 A
i_d = i_0/4 = 1 A
i_8Ω = 8/8 = 1 A
4 + 1 + 1 = 6 A ✓
The branch currents exactly equal the 6 A source current, confirming the node equation and the final answer.
Concept Extension
Dependent sources remain active during normal circuit analysis. Their controlling relationship is part of the circuit physics. The fastest safe workflow is: choose node voltage → write controlling variable → write dependent source → apply KCL → calculate the requested power.
Exam Strategy
When many branches share the same two nodes, first test whether a single-node KCL equation can solve the problem. It is often much faster than mesh analysis.
Quick Trick
Same two nodes → one V. i₀ = V/2, dependent = V/8, 8 Ω current = V/8. KCL → V = 8 V → P = 8 W.
Why Other Options Are Wrong
- B — 16 W: would require |V| = √(16×8) ≈ 11.31 V, which does not satisfy KCL.
- C — 32 W: would require |V| = 16 V, inconsistent with the 6 A source and branch currents.
- D — 64 W: would require |V| ≈ 22.63 V, also impossible from the KCL relation.
Common Mistake
Ignoring the arrow direction, forgetting i₀ = V/2, or using i₀/4 as a constant current independent of V.

આકૃતિ Q4માં દર્શાવેલા પરિપથમાં 8 Ω અવરોધકમાં વ્યય થતા પાવરની ગણતરી કરો.
જવાબ અને પગલાવાર ઉકેલ
A — 8 W. ચારેય શાખાઓ એ જ બે નોડ વહેંચે છે, તેથી એક નોડ-વોલ્ટેજ સમીકરણ પૂરતું છે. ઉપરના નોડનું વોલ્ટેજ V હોય તો i₀ = V/2, આધારિત સ્રોત પ્રવાહ = V/8 અને 8 Ω પ્રવાહ = V/8. KCLથી V = 8 V, તેથી P = V²/8 = 8 W.
વિગતવાર ઉકેલ (મૂળ ભાષામાં)
Concept Foundation — Why Nodal Analysis Is Ideal Here
Every element in Fig. Q4 is connected between the same top node and the same bottom reference node. That means every branch has the same voltage. Instead of writing several loop equations, define one node voltage V and express each branch current in terms of V.
The circuit also contains a dependent current source . A dependent source is not assigned an arbitrary current; its value must always be written from its controlling variable. Here the controlling current is i₀ through the 2 Ω resistor.
Step 1 — Define the Node Voltage and Controlling Current
Take the bottom conductor as reference (0 V) and the top conductor as V volts. The current i₀ is shown downward through the 2 Ω resistor, so by Ohm’s law:
i_0 = V/2
Step 2 — Express the Dependent Source
The dependent current source arrow is downward and its value is i₀/4. Therefore:
i_d = i_0/4 = (V/2)/4 = V/8
Step 3 — Express the 8 Ω Branch Current
i_8Ω = V/8
Step 4 — Apply KCL at the Top Node
The 6 A source injects current upward into the top node. The three right-hand branch currents leave the top node downward. Hence incoming current = outgoing current:
6 = V/2 + V/8 + V/8
6 = 4V/8 + V/8 + V/8
6 = 6V/8 = 3V/4
V = 8 V
Step 5 — Calculate Power in the 8 Ω Resistor
P = V²/R
P_8Ω = 8²/8 = 8 W
KCL Cross-Check
i_0 = 8/2 = 4 A
i_d = i_0/4 = 1 A
i_8Ω = 8/8 = 1 A
4 + 1 + 1 = 6 A ✓
The branch currents exactly equal the 6 A source current, confirming the node equation and the final answer.
Concept Extension
Dependent sources remain active during normal circuit analysis. Their controlling relationship is part of the circuit physics. The fastest safe workflow is: choose node voltage → write controlling variable → write dependent source → apply KCL → calculate the requested power.
Exam Strategy
When many branches share the same two nodes, first test whether a single-node KCL equation can solve the problem. It is often much faster than mesh analysis.
Quick Trick
Same two nodes → one V. i₀ = V/2, dependent = V/8, 8 Ω current = V/8. KCL → V = 8 V → P = 8 W.
Why Other Options Are Wrong
- B — 16 W: would require |V| = √(16×8) ≈ 11.31 V, which does not satisfy KCL.
- C — 32 W: would require |V| = 16 V, inconsistent with the 6 A source and branch currents.
- D — 64 W: would require |V| ≈ 22.63 V, also impossible from the KCL relation.
Common Mistake
Ignoring the arrow direction, forgetting i₀ = V/2, or using i₀/4 as a constant current independent of V.