Consider the following statements with reference to Protective Relays:1.The minimum relay coil current at which the relay operates is called pick-up value.2.The pick-up value of a relay is 7.5 A and fault current is 30 A. Therefore its plug setting multiplier is5.3. An earth fault current is generally lesser than the short-circuit current.4.Induction relays are used with both A.C. and D.C quantities.Which of these statements are correct?
⚑ Report issue
Found a wrong answer, translation, image or source problem? Send it to editorial review.
Plug setting multiplier is the fault current divided by relay pickup current. PSM=I_fault/I_pickup=30/7.5=4, so the statement claiming 5 is numerically incorrect. Key relation: PSM=I_fault/I_pickup.
Exam focus: Calculate PSM numerically before selecting an option. Common trap: Induction-type relays are not used directly on DC quantities.
Formula / Key Relation
PSM=Ifault/Ipickup.
Detailed Explanation
Correct Answer: D - 1 and 3 only Quick Concept Explanation Plug setting multiplier is the fault current divided by relay pickup current. PSM=I_fault/I_pickup=30/7.5=4, so the statement claiming 5 is numerically incorrect. Key relation: PSM=I_fault/I_pickup.Exam focus: Calculate PSM numerically before selecting an option. Common trap: Induction-type relays are not used directly on DC quantities. Statement-wise Verification Statement 1 - Correct.The minimum relay coil current at which the relay operates is called pick-up value.Plug setting multiplier is the fault current divided by relay pickup current. Statement 2 - Incorrect.The pick-up value of a relay is 7.5 A and fault current is…
Correct Answer: D - 1 and 3 only
Quick Concept Explanation
Plug setting multiplier is the fault current divided by relay pickup current. PSM=I_fault/I_pickup=30/7.5=4, so the statement claiming 5 is numerically incorrect. Key relation: PSM=I_fault/I_pickup.
Exam focus: Calculate PSM numerically before selecting an option. Common trap: Induction-type relays are not used directly on DC quantities.
Statement-wise Verification
Statement 1 - Correct. The minimum relay coil current at which the relay operates is called pick-up value. Plug setting multiplier is the fault current divided by relay pickup current.
Statement 2 - Incorrect. The pick-up value of a relay is 7.5 A and fault current is 30 A. Therefore its plug setting multiplier is 5. 3. An earth fault current is generally lesser than the short-circuit current. 4. Induction relays are used with both A.C. and D.C quantities. PSM=30/7.5=4, not 5
Statement 5 - Review. 3. An earth fault current is generally lesser than the short-circuit current. Earth-fault current is often lower than a three-phase short-circuit current because the zero-sequence path adds impedance.
Statement 4 - Review. Induction relays are used with both A.C. and D.C quantities. Induction relays require alternating flux and are AC devices.
Core Concept
Protective-relay pickup is the minimum actuating quantity that causes operation. Plug setting multiplier is the fault current divided by relay pickup current. Earth-fault current is often lower than a three-phase short-circuit current because the zero-sequence path adds impedance. Induction relays require alternating flux and are AC devices.
Formula / Key Relationship
PSM=I_fault/I_pickup.
Step-by-Step Check
PSM=I_fault/I_pickup=30/7.5=4, so the statement claiming 5 is numerically incorrect.
Why the Other Options Are Wrong
Option A is incorrect because it includes incorrect statement(s) 2 and omits correct statement(s) 3. Option B is incorrect because it includes incorrect statement(s) 2 and omits correct statement(s) 1. Option C is incorrect because it includes incorrect statement(s) 2, 4 and omits correct statement(s) 3.
Exam Shortcut / Approach
Calculate PSM numerically before selecting an option.
Common Mistake
Induction-type relays are not used directly on DC quantities.
Quick Revision
Pickup PSM Earth Fault and Induction Relay is linked with Protective Relays, Protection and Power Systems. Calculate PSM numerically before selecting an option.
Quick Trick
Calculate PSM numerically before selecting an option.
Why Other Options Are Wrong
Option A is incorrect because it includes incorrect statement(s) 2 and omits correct statement(s) 3. Option B is incorrect because it includes incorrect statement(s) 2 and omits correct statement(s) 1. Option C is incorrect because it includes incorrect statement(s) 2, 4 and omits correct statement(s) 3.
Common Mistake
Induction-type relays are not used directly on DC quantities.
Exam Tip
Calculate PSM numerically before selecting an option.