Q107EasyDistribution Systems

वितरण प्रणाली में उपयुक्त स्थानों पर इष्टतम आकार के संधारित्र लगाने का परिणाम है
1. बेहतर वोल्टेज नियमन
2. वितरण शक्ति हानि में कमी
3. वितरण ट्रांसफार्मरों की kVA रेटिंग में कमी
नीचे दिए गए कूटों का उपयोग करके सही उत्तर चुनिए:

उत्तर और चरणबद्ध हल
सही उत्तर: B. 1, 2 और 3
संक्षिप्त व्याख्या

B — 1, 2 और 3। शंट संधारित्र PF सुधारते हैं, जिससे समान kW पर धारा घटती है (I = P/(V·PF)) — फलतः kVA माँग, ट्रांसफार्मर kVA रेटिंग और I²R हानि घटती है और वोल्टेज नियमन सुधरता है।

विस्तृत हल (मूल भाषा में)

Statement-wise Verification

  • Statement 1 - Correct.
    improved voltage regulation
    Raising power factor with shunt capacitors or an over-excited synchronous machine reduces kVA demand, line current and I²R losses and generally improves voltage regulation.
  • Statement 2 - Correct.
    reduction in distribution power losses
    Raising power factor with shunt capacitors or an over-excited synchronous machine reduces kVA demand, line current and I²R losses and generally improves voltage regulation.
  • Statement 3 - Correct.
    reduction of kVA rating of distribution transformers
    Raising power factor with shunt capacitors or an over-excited synchronous machine reduces kVA demand, line current and I²R losses and generally improves voltage regulation.

Core Concept

For a fixed real-power load and supply voltage, poor power factor requires higher current. Raising power factor with shunt capacitors or an over-excited synchronous machine reduces kVA demand, line current and I²R losses and generally improves voltage regulation. Compensation should be placed close to the inductive load when practical so reactive current does not travel through upstream conductors.

Formula / Key Relationship

Single phase: I=P/(V·PF). Three phase: I=P/(√3 V_L·PF).

Why the Other Options Are Wrong

Option A is incorrect because it omits correct statement(s) 2, 3. Option C is incorrect because it omits correct statement(s) 3. Option D is incorrect because it omits correct statement(s) 1, 2.

Exam Shortcut / Approach

For the same kW, current is inversely proportional to power factor.

Common Mistake

Capacitors supply leading reactive power; they do not supply lagging VARs.

Quick Revision

Capacitor Placement in Distribution is linked with Shunt Capacitors, Distribution Systems and Power Systems. For the same kW, current is inversely proportional to power factor.